EXIN EPI Certified Data Centre Specialist Questions and Answers

Question 17

The UPS of a data center, with an ANSI/TIA-942 Rating-4, is installed with the rectifier connected to power feed A and the bypass/reserve line input connected to power feed B.

To which feed will the output of the UPS be synchronized?

Options:

A.

The UPS will not synchronize to any of the feeds but use an internal clock to set the output voltage and frequency

B.

Depends on the setting of the UPS, as the UPS can normally be set to either feed

C.

Feed A

D.

Feed B

Question 18

Which class of UPS is ideal for data centers?

Options:

A.

VFD (Voltage and Frequency Dependent)

B.

VI (Voltage Independent)

C.

VFI (Voltage and Frequency Independent)

D.

First class

Question 19

What is the advantage of OM5 multimode fiber cabling?

Options:

A.

Supports SWDM, requiring fewer fibers

B.

No advantage—same as OM4

C.

Designed for cheaper LED transmitters

D.

100 Gbit/s link for 500 m reach

Question 20

It is assumed that EMF shielding material must be installed as the EMF levels coming from the transformer room into the computer room are measured at 100mG. The transformer room is approximately 10 meters away from the computer room and is separated by a corridor. You can assume that no physical issues are present for installing shielding material at any area/location.

Where should you recommend the shielding material to be installed?

Options:

A.

As close as possible to the computer room

B.

As close as possible to the transformer room

C.

It does not matter, either close to the transformer room or the computer room is okay as there is no impact to cost or shielding material performance

D.

Shielding is not required to be installed as 100mG is within the acceptable levels for computer rooms