Concealed connections in Type IV-C construction require periodic special inspection under 2021 IBC Table 1705.5.3, making option B correct.
The mass timber special-inspection table specifically applies to mass timber elements in Types IV-A, IV-B, and IV-C . Among the activities listed for periodic inspection are bolted connections, concealed connections, erection of mass timber construction, screw installation, verification of required predrilling, and several other connection-related installation characteristics.
Options A and C are incorrect because they specify Type IV-HT. Table 1705.5.3 is expressly scoped to Types IV-A, IV-B, and IV-C rather than Type IV-HT. Option D involves a listed Type IV-A activity, but its inspection frequency is wrong: adhesive anchors installed horizontally or upwardly inclined to resist sustained tension loads require continuous , not periodic, special inspection.
For concealed connections, inspection must occur while the relevant components remain observable. Once CLT panels, wood cover, gypsum protection, or finishes hide the connection, critical installation details may no longer be verifiable without destructive removal.
References/Topics: 2021 IBC Section 1705.5.3 and Table 1705.5.3, Required Special Inspections of Mass Timber Construction.
===============