HCSP-Field-Data Center Facility V1.0 Questions and Answers
Question 17
In alarm management, the status can be identified by masking rules.
Options:
A.
Invalid
B.
Standard
C.
Maintenance
D.
Valid
Answer:
A, C
Explanation:
In Huawei alarm management,masking rulesare used to control how alarms are handled and displayed during specific conditions, such as planned maintenance, commissioning, device replacement, or known temporary abnormalities. When a masking rule is applied, the system can change how an alarm is classified so that O&M staff can distinguish between alarms that require immediate action and alarms that are expected or should be excluded from operational statistics. Two key statuses that masking rules can assign areMaintenanceandInvalid.Maintenanceindicates the alarm is generated during an approved maintenance activity (for example, power-off tests, sensor rewiring, cooling maintenance), so it is treated as expected and does not trigger normal escalation logic.Invalidindicates the alarm is not considered effective for operational follow-up—commonly used when a point is confirmed to be non-applicable, temporarily disabled, or its triggering condition is not meaningful to current operations. By contrast,ValidandStandardrepresent normal alarm handling states rather than outcomes specifically “identified by masking rules.”
Question 18
If a component runtime overdue alarm is generated for an air conditioner, you can clear the device running time on the "Maint > Performance Maintenance" screen.
Options:
A.
True
B.
False
Answer:
A
Explanation:
Huawei smart cooling/precision air-conditioning controllers manage preventive maintenance by trackingaccumulated runtimefor wear components such as indoor fans, compressors (where applicable), humidifiers, and pumps. When a component reaches its configured maintenance interval, the controller generates aruntime overdue alarmto remind O&M staff to inspect, service, or replace the component. After the required maintenance action is completed (for example, fan replacement, bearing inspection, cleaning, or pump servicing), the accumulated runtime record must becleared/resetso the next maintenance cycle can be measured correctly from zero. The controller provides this function under the maintenance feature set because it is part of lifecycle management and performance tracking rather than an alarm acknowledgement. The navigation pathMaint > Performance Maintenanceis used to access runtime statistics and to clear the corresponding device/component running time after maintenance. This avoids repeated overdue alarms for a component that has already been serviced and ensures future alarms accurately reflect the operating hours of the newly serviced or replaced parts, improving reliability and maintenance planning accuracy.